A 3-phase transformer rated for 33 kV/11 kV is connected in delta/star as shown in figure. The current transformers (CTs) on low and high voltage sides have a ratio of 500 / 5. Find the currents i1 and i2 , if the fault current is 300A as shown in figure.
-
- i1 = 1 / √3 A , i2 = 0A
- i1 = 0 A , i2 = 0 A
- i1 = 0 A , i1 = 1 / √3 A
- i1 = 1 / √3 A , i2 = 1 / √3 A
Correct Option: A
i2 = 0 (∵ entire current flows through fault)
Now, Primary kVA = Secondary kVA
∴ √3 × IL = √3 × 11000 × | ![]() | 300 × | ![]() | ||
500 |
I L = 1A
Now, IL = √3 IPh
∴ IPh = | = | A | ||
√3 | √3 |