A cylindrical rotor generator delivers 0.5 pu power in the steady-state to an infinite bus through a transmission line of reactance 0.5 pu. The generator no-load voltage is 1.5 pu and the infinite bus voltage is 1 pu. The inertia constant of the generator is 5 MW-s/MVA and the generator reactance is 1 pu. The critical clearing angle, in degrees, for a three-phase dead short circuit fault at the generator terminal is
-
- 53.5
- 60.2
- 70.8
- 79.6
Correct Option: C
A1 = Accelerating area, δcr = critical clearing angle
A2 = Decelerating area.
Equal area acceleration states that for stability A1 = A2
⇒ Peo(δcr - δo) =
⇒ Peo (δcr - δo) = Pmax(cos δcr - cos δmax) - Peo (δmax - δcr)
⇒ Peo (δcr - δo) + Pmax cos δmax = Pmax cos δcr
⇒ cos δcr = | (δmax - δo) + cos δmax | |
Pmax |
δmax = | ![]() | π - | ![]() | rad = 2.61 rad | |
180° |
then, cos δcr = 0.5 (2.61 – 0.52) + cos 150° = 0.179
δcr = cos– 1 0.179 = 79.6°