The figure shows a two-generator system supplying a load of PD = 40 MW, connected at bus 2.
The fuel cost of generators G1 and G2 are :
C1 (PG1) = 10,000 Rs/MWh and C2 (PG2) = 12,500 Rs/MWh
and the loss in the line is Ploss(pu) = 0.5 PG1(pu) 2,
where the loss coefficient is specified in pu on a 100 M VA base. The most economic power generation schedule in MW is
-
- PG1 = 20, PG2 = 22
- PG1 = 22, PG2 = 20
- PG1 = 20, PG2 = 20
- PG1 = 0, PG2 = 40
Correct Option: B
PL = 0.5 PG12
PL is given by,
PL = B11 PG12 + 2B12 PG1 PG2 + PG22 B22
where B11, B12 & B22 are loss - coefficients.
Since load PD is connected to Bus 2,
B22 = B12 = 0.
Now , | = 2 × 0.5 PG1 = PG1 | |
∂PG1 |
and | = 0 | |
∂PG2 |
Penality factors, L1 = | = | |||||
1 - | 1 - PG1 | |||||
∂PG1 |
and L2 = | = 1 | ||||
1 - | |||||
∂PG1 |
Now, L1 .C1 (PG1) = L2 C2 (PG2) = λ
⇒ | × 10000 = 1 × (12500) | |
1 - PG1 |
⇒ PG1 = 0.2 P.U.
⇒ PG1 = 20 MW
As, PG1 + PG2 = PD + PL = PD + 0.5 PG12
⇒ 20 + PG1 = 40 + 0.5 × (0.2)2 × 100
⇒ PG2 = 22 MW