The core loss of a single phase, 230/115 V, 50Hz power transformer is measured from 230 V side by feeding t he pr imar y (230 V side) fr om a variable voltage variable frequency source while keeping the secondary open circuited. The core loss is measured to be 1050 W for 230 V, 50 Hz input. The core loss is again measured to be 500 W for 138 V, 30 Hz input. The hysteresis and eddy current losses of the transformer for 230 V, 50Hz input are respectively.
-
- 508 W and 542 W
- 468 W and 582 W
- 498 W and 552 W
- 488 W and 562 W
Correct Option: A
1 - φ | , 50 Hz | |
115 V |
Core loss = 1050 W at 230V, 50Hz
Core loss = 500W at 138V, 30 Hz
In both cases | ratio is constant | |
f |
Hence,

At 50 Hz ⇒ 1050 = A (50) + B(50)2
At 30 Hz ⇒ 500 = A (30) + B(30)2
A = 10.167
B = 0.217
∴ Wn at 50Hz = (10.167) × 50 = 508 W
Wc at 50 Hz = (0.217) × (50)2 = 542 W