Home » Power Systems » Power systems miscellaneous » Question
  1. What is the corona loss of a 3 – φ line, 160 km long, conductor diameter 1.036 cm, 2.44 delta spacing, air temperature 26°, corresponding to a barometric pressure of 72 cm, operating voltage 110 kV at 50 Hz. m = 0.78?
    1. 322 kW
    2. 792 kW
    3. 800 kW
    4. 841 kW
Correct Option: D

Here, L = 160 km; diameter = 1.036;
d = 2.44 m; r = 0.518 cm = 0.518 × 10-2m

δ =
3.92 b
=
3.92 × 72
= 0.943
273 + t273 + 26

∴ Vd = 21.1 × 0.78 × 0.943 × 0.518
In
2.44
× 100 = 8.039 × In
244
= 49.47 (Line to neutral) kV.
0.5180.518

Power Loss
= 241 × 10-5
ƒ + 25
× √
r
(V - Vd)²kW/phase/km.
δd

= 241 × 105
50 + 25
× √
0.518
× 100(63.5 - 9.4)²
0.9432.44

= (0.1916 × 0.046 × 198.81) = 1.75 kW/phase/km.
= 5.25 kW/km.
= 841 kW for three phases.