Home » Power Systems » Power systems miscellaneous » Question
  1. A 3φ, 50 Hz, 132 kV transmission line consists of conduct or of 1.17 cm diameter and spaced equilaterely at a distance of 3m. The line conductors have smooth surface with value for m = 0.96. The barometric pressure is 72 cm of Hg and temperature of 20°C. The corona loss in foul weather condition will be
    1. 3.12 kW/km/phase
    2. 4.84 kW/km/phase
    3. 8.70 kW/km/phase
    4. none of these
Correct Option: A

Diameter =1.17 cm; r = 0.585 cm; d = 3 m

d
=
300
= 512.8
r0.585

or √
r
= √
1
= 0.044
d512.8

δ =
3.92 × b
=
3.92 × 72
= 0.96
273 + t293

V =
132
= 76.21 kV/phase
3

∴ Vd = 21.1 × 0.96 × 0.96 × 0.585 ln (512.8)
= 70.98 kV (line to neutral)
Corona loss under foul weather condition will be when the disruptive voltage is taken as
Vd = 0.8 × fair weather value
= 0.8 × 70.98 = 56.78
PC = 241 × 10–5
ƒ + 25
× √
r
(V - Vd)
6d

= 241 × 10–5 ×
75
× √
1
(76.21 - 56.78)
0.96512.8

= 3.12 k W/k m/phase