A 50 Hz balanced three-phase, Y-connected supply is connected to a bal anced three-phase Y-connected load. If the instantaneous phase -a of the supply voltage is Vcos (ωt) and the phase-a of the load current is Icos (ωt – φ), the instantaueous three-phase power is
-
- a constant with a magnitude of VI cos φ
- a constant with a magnitude of (3/2)VI cos φ
- time-varying with an aver age value of (3/2)VI cos φ and a frequency of 100 Hz.
- time-varying with an average value of VIcos φ and a frequency of 50 Hz.
Correct Option: B
Total power transmitted = Sum of the individual powers in each phase
P = Vaia + Vbib + Vcic
= V cosωt · I cos (ωt – φ) + V cos (ωt – 120°) · I cos (ωt – 120° – φ) + V cos (ωt + 120°) cos (ωt + 120° – φ)
[cos 2 ωt + cos φ + cos (2ωt – 240° – φ) + cos φ + cos (2ωt + 240° – φ) + cos φ] | |
2 |
[cos (2ωt – φ) + 3cos φ + cos (2ωt – φ) + cos 240° – sin (ωt – φ) sin 240 + cos (2ωt – φ) cos 240° + sin (2ωt – φ) sin 240°] | |
2 |
[cos (2ωt - φ) + 3 cos φ - cos (2ωt -φ)] | |
2 |
3 | cosφ . | |
2 |