  1. A fault occuring at the terminals of an unloaded synchronous generator opetaing at its rated voltage has resulted in the following values of the current and voltage.
    Ia0 = j 2.37 p.u.
    Ia1 = j 3.05 p.u.
    Ia2 = j 0.68 p.u.
    Va0 = Va1 = Va2 = j 2.37 p.u.
    The fault that has occurred is
    1. L– L fault
    2. L– L– G fault
    3. L– G fault
    4. none of these
Correct Option: B