A fault occuring at the terminals of an unloaded synchronous generator opetaing at its rated voltage has resulted in the following values of the current and voltage.
Ia0 = j 2.37 p.u.
Ia1 = j 3.05 p.u.
Ia2 = j 0.68 p.u.
Va0 = Va1 = Va2 = j 2.37 p.u.
The fault that has occurred is
-
- L– L fault
- L– L– G fault
- L– G fault
- none of these
Correct Option: B