  1. A 3 – φ induction motor takes 100 kW at 415 V, 50 Hz and a power factor of 0.80 lagging. What is the kVAr rating of a capacitor bank to improved the power factor to 0.9 lagging, if the capacitor bank is connected to delta ?
    1. 6.25
    2. 7.99
    3. 7.91
    4. 8.82
Correct Option: D

Power per phase =
100
= 33.33 kW
3

Power factore, cos φ1 = 0.8
⇒ φ1 = 36.85°
∴ tan φ1 = 0.749
Final power factor,
cos φ2 = 0.9
⇒ φ2 = 25.84°
∴ tan φ2 = 0.4843
Reactive power, Qcp = PP (tan φ1 – tan φ2)
=
100
(0.749 – 0.4843)
3

= 8.82 kVAr/phase