  1. A 3 – φ induction motor takes 120 kW at 415 V, 50 Hz and a power factor of 0.8 lagging. What is the capacitance per phase, if its power factor is improve to 0.9 and capacitor bank is connected in star ?
    1. 587 µF
    2. 440 µF
    3. 560 µF
    4. 600 µF
Correct Option: A

Power per phase,

PP =
120
= 40 kW
3

cos φ1 = 0.8
⇒ φ1 = 36.86°
∴ tan φ1 = 0.749
Final power factor,
cos φ2 = 0.9
⇒ φ2 = 25.84°
∴ tan φ2 = 0.4843
Now QCP = PP (tan φ1 – tan φ2)
= 40 (0.749 – 0.4843)
= 10.588 KVAr/phase.
VP =
VL
=
415
= 239.6 volts
33

IC =
QC
=
10.588 × 1000
= 44.19 Ampere
VP239.6

Capacitance per phase,
CY =
IC
=
IC
ω . VP2πƒ . VP

=
44.19
= 587.0 × 10-6 F
2π × 50 × 239.6

= 587 µF