Home » Power Systems » Power systems miscellaneous » Question
  1. A sustained t hr ee-phase fault occurs in the power system shown in the figure. The current and voltage phasors during the fault (on a common reference), after the natural transients have died down, are also shown. Where is the fault located?
    1. Location P
    2. Location Q
    3. Location R
    4. Location S
Correct Option: B