					 A 3-phase transmission line is shown in the figure. Voltage drop across the transmission line is given by the following equation:

Shunt capacitance of the line can be neglected. If the line has positive sequence impedance of 15 Ω and zero sequence impedance of 48 Ω, then the values of Zs and Zm will be
 
- 
                        
- Zs = 31.5 Ω; Zm = 16.5 Ω
 - Zs = 26 Ω; Zm = 11Ω
 - Zs = 16.5 Ω; Zm = 31.5 Ω
 - Zs = 11 Ω; Zm = 26 Ω
 
 
Correct Option: B
 For the given system, the relationship between sequence impedance and Zs, Zm is given by Positive sequence impedance, 
Z1 = Zs – Zm . 
Negative sequence impedance, 
Z2 = Zs – Zm . 
Zero sequence impedance, 
Z0 = Zs – 2Zm . 
Given Zs – Zm = 15 
and Zs + 2Zm = 48 
Solving, we get, 
Zs = 26, Zm = 11