A lossless power system has to serve a load of 250 MW. There are two generators (G1 and G2) in the system with cost curves C1 and C2 respectively defined as follows:
C1 (PG1) = PG1 + 0.055 × PG1²
C2 (PG2) = 3PG2 + 0.03 × PG2²
where PG1 and PG2 are the MW injections from generator G1 and G2 respectively. Then the minimum cost dispatch will be
-
- PG1 = 250 MW; PG2 = 0 MW
- PG1 = 150 MW; PG2 = 100 MW
- PG1 = 100 MW; PG2 = 150 MW
- PG1 = 0 MW; PG2 = 250 MW
Correct Option: C
C1 (PG1) = PG1 + 0.055 × PG1²
∴ | = 1 + 0.11PG1 | |
dPG1 |
C2 (PG2) = PG2 + 0.03 × PG2²
∴ | = 3 + 0.06 PG2 | |
dPG2 |
For minimum cost analysis
= | |||
dPG1 | dPG2 |
⇒ 1 + 0.11 PG1 = 3 + 0.006 PG2
or 0.11 PG1 – 0.06 PG2 = 2 ...(1)
and PG1 + PG2 = 250 MW ...(2)
Solving equations (1) and (2), we get
PG1 = 100 MW and PG2 = 150 MW