  1. A lossless power system has to serve a load of 250 MW. There are two generators (G1 and G2) in the system with cost curves C1 and C2 respectively defined as follows:
    C1 (PG1) = PG1 + 0.055 × PG1²
    C2 (PG2) = 3PG2 + 0.03 × PG2²
    where PG1 and PG2 are the MW injections from generator G1 and G2 respectively. Then the minimum cost dispatch will be
    1. PG1 = 250 MW; PG2 = 0 MW
    2. PG1 = 150 MW; PG2 = 100 MW
    3. PG1 = 100 MW; PG2 = 150 MW
    4. PG1 = 0 MW; PG2 = 250 MW
Correct Option: C

C1 (PG1) = PG1 + 0.055 × PG1²

dC1
= 1 + 0.11PG1
dPG1

C2 (PG2) = PG2 + 0.03 × PG2²
dC2
= 3 + 0.06 PG2
dPG2

For minimum cost analysis
dC1
=
dC2
dPG1dPG2

⇒ 1 + 0.11 PG1 = 3 + 0.006 PG2
or 0.11 PG1 – 0.06 PG2 = 2 ...(1)
and PG1 + PG2 = 250 MW ...(2)
Solving equations (1) and (2), we get
PG1 = 100 MW and PG2 = 150 MW