  1. A 3-phase balanced load which has a power factor of 0.707 is connected to balanced supply. The power consumed by t he load is 5kW. The power is measured by the two-wattmeter method. The readings of the two wattmeters are
    1. 3.94 kW and 1.06 kW
    2. 2.50 kW and 2.50 kW
    3. 5.00 kW and 0.00 kW
    4. 2.96 kW and 2.04 kW
Correct Option: A