  1. In a wastewater treatment plant, primary sedimentation tank (PST) designed at an overflow rate of 32.5 m³/day/m² is 32.5 m long, 8.0 m wide and liquid depth of 2.25 m. If the length of the weir is 75 m, the weir loading rate (in m³/day/m) is
    1. 111.67 m³/d/m
    2. 110.67 m³/d/m
    3. 109.67 m³/d/m
    4. 112.67 m³/d/m
Correct Option: D

112.67
SOR = 32.5 m³/d/m²
L = 32.5 m
B = 8 m, D = 2.25 m

SOR =
Q
BL

∴ Q = SOR × B.L
= 32.5 × 8 × 32.5
= 8450 m³/d
q =
Q
b

b = 75 m (weir length)
q =
8450
75

= 112.67 m³/d/m