  1. A building has to be maintained at 21 °C (dry bulb) and 14.5°C(wet bulb). The dew point temperature under these conditions is 10.17°C. The outside temperature is –23°C (dry bulb) and the internal and external surface heat transfer coefficients are 8 W/m2K and 23 W/ m2K respectively. If the building wall has a thermal conductivity of 1.2 W/mK, the minimum thickness (in m) of the wall required to prevent condensation is
    1. 0.471
    2. 0.407
    3. 0.321
    4. 0.125
Correct Option: B