A 3– phase delta/star transformer is supplied at 6000 V on the delta-connected side. The terminal voltage on the secondary side when supplying full load at 0.8 lagging power-factor is 415 V. The equivalent resistance and reactance drops for the transformer are 1% and 5% respectively. The turns ratio of the transformer is _______ .
-
- 4
- 24
- 12
- All of the above
Correct Option: B
Turn ratio = | |
Phase voltage on secondary side |
= | = 24 | |
415 |