A single - phase 50 – kVA, 250V/ 500 V two winding transformer has an efficiency of 95% at full load, unity power factor. If it is reconfigured as a 500 V/ 750 V auto-transformer, its efficiency at its new rated load at unity power factor will be
-
- 95.752%
- 97.851%
- 98.276%
- 99.241%
Correct Option: C
Efficiency , η = 0.95 = | ||
50 + Losses |
⇒ Losses = 50 – 47.5 = 2.5 kW
Now kVA = 50 × | ||
1 - K |
K = | = | |||
750 | 3 |
= 50 × | = 50 | |
{1 - (2 / 3)} |
∴ New efficiency = | × 100 = 98.36% | |
150 + 2.5 |