Two single-phase transformers T1 and T2 each rated at 500 k VA are operated in parallel. Percentage impedances of T1 & T2 are (1 + j6) and (0.8 + j4.8) respectivel y. To share a load of 1000 k VA at 0.8 lagging power factor, the contribution of T2 (in kVA) is _________.
-
- 614
- 525
- 555
- None of these
Correct Option: C
ST2 = S × | ||
z1 + z2 |
= 1000 × | = 555 KVA | |
10.94 ∠ 80.53 |