  1. A three phase circuit line consists of 7/4.75 mm hard drawn copper conductors. The arrangement is shown in the figure. The line is completely transposed. What is the inductance, per phase per km of the system?
    1. 0.90 mH/km
    2. 0.21 mH/km
    3. 0.57 mH/km
    4. 0.64 mH/km
Correct Option: D

Diameter of each conductor = 3 × 4.75 = 14.25 mm.
r = 7.125 × 10-3 m.
Dab = √3² + 1.5² = 3.354 m
Dbc = Da'b' = Db'c' = 3.354 m
Dab' = √3² + 7.5² = 8.077 m
Dbc' = Dba' = Db'c = Dab' = 8.077 m
Daa' = √6² + 6² = 6√2 m
Dcc' = 6√2 m
Dm = (Dab.Dbc.Dca.Dab'.Db'c.Dc'a.Da'b'.Db'c'.Dc'a'.)1/2
= (3.354 × 3.354 × 6 × 8.076 × 8.076 × 6 × 8.076 × 8.076 × 6 × 3.354 × 3.54 × 6)1/12
= 5.4576 m
DsL = (r'³ × Daa' × Dbb' × Dcc')1/6
= [(0.7788 × 7.125 × 10-3)³ × 6√2 × 9 × 6√2]1/6
= 0.21913 m

= 2 × 10-7 In
Dm
DsL

= 2 × 10-7 In
5.4576
H/m
0.21913

= 6.43 × 10-7 H/m = 6.43 × 10-4 H/km = 0.643 mH/k m.