  1. A 3 – φ load of 750 kW at 400 V, 50 Hz, operates at a power factor of 0.7 lagging. What is the capacitance per phase of a mesh connected capacitor bank to improve the power factor to 0.95 lagging?
    1. 3040 µF
    2. 2500 µF
    3. 3438 µF
    4. 2789 µF
Correct Option: C

Power per phase,

PPh =
750
= 250 kW
3

cos φ1 = 0.7
⇒ φ1 = 45.57°
∴ tan φ1 = 1.02
Improved, cos φ2 = 0.95;
⇒ φ2 = 18.19°
∴ tan φ2 = 0.3286
Qcp = PP (tan φ1 – tan φ2)
= 250 (1.02 – 0.3286)
= 172.83 kVAr/ phase
Now QC = V.IC
Here,
IC =
V
= V.ωC
XC

∴ QC = V².ωC
⇒ C =
QC
V².ω