A 3 – φ load of 750 kW at 400 V, 50 Hz, operates at a power factor of 0.7 lagging. What is the capacitance per phase of a mesh connected capacitor bank to improve the power factor to 0.95 lagging?
-
- 3040 µF
- 2500 µF
- 3438 µF
- 2789 µF
Correct Option: C
Power per phase,
PPh = | = 250 kW | |
3 |
cos φ1 = 0.7
⇒ φ1 = 45.57°
∴ tan φ1 = 1.02
Improved, cos φ2 = 0.95;
⇒ φ2 = 18.19°
∴ tan φ2 = 0.3286
Qcp = PP (tan φ1 – tan φ2)
= 250 (1.02 – 0.3286)
= 172.83 kVAr/ phase
Now QC = V.IC
Here,
IC = | = V.ωC | |
XC |
∴ QC = V².ωC
⇒ C = | ||
V².ω |