  1. The incremental cost characteristics of the two units in a plant are given by
    IC1 = Rs (0.1 P1 + 8.0) per MWh
    IC2 = Rs (0.15 P2 + 3.0) per MWh
    The optimum sharing of load when the total load is 100 MW is
    1. P1 = 60 MW and P2 = 40 MW
    2. P1 = 33.3 MW and P2 = 66.7 MW
    3. P1 = 40 MW and P2 = 60 MW
    4. P1 = 66.7 MW and P2 = 33.3 MW
Correct Option: C

At optium sharing, IC1 = IC2.
The two equations can easily be solved with the constraint P1 + P2 = 100 MW
∴ P1 = 40 MW,
and P2 = 60 MW.