  1. The following sequence currents were recorded in a power system under a fault condition:
    Ipositive = j 1.653 p.u.
    Inegative = – j 0.5 p.u.
    Izero = – j 1.153 p.u.
    The fault is
    1. line to ground
    2. three phase
    3. line to line ground
    4. line to line
Correct Option: C

We see that all the sequence components are non-zero and
Ia = Ia0 + Ia1 + Ia2
= – j 1.153 + j 1.653 – j 0.5 = 0
We conclude that it is a L-L-G fault.