The following figure shows the single line diagram of a power system with all reactances marked in per unit (p.u.) on the same base:
The system is on no-load when a 3-phase fault occurs at ‘F’ on the high voltage side of the transformer T2. The fault current will be
-
- – j 0.8187 p.u.
- + j 0.8187 p.u.
- – j 8.1871 p.u.
- + j 8.1871 p.u.
Correct Option: C
The reactance diagram of the system is as shown. Drawing the Thevenin’s equation circuit, we have VTh = 1.0 p.u.
ZTh = j | = j 0.122 p.u. | |
0.56 |
∴ jF = | = -j 8.1871 p.u. | |
j0.122 |