Home » Power Systems » Power systems miscellaneous » Question
  1. A three phase 50 Hz line consists of three conductors each of diameter 21 mm. The spacing between the conductors as follows: A – B = 3m, B – C = 5m, C – A = 3.6 m
    If the line operates at 132 kV, the reactive voltampere generatd by the line per km is _______kVAr
    1. 51703 VAr.
    2. 5.1703 VAr.
    3. 517.03 VAr.
    4. 5170.3 VAr.
Correct Option: A

Cn =
2πε0
=
1
= 9.43 × 10-9 F/km
In
Dm
18 × 109 × In
3 × 5 × 3.6
1/3
DsL
2

Xc =
1
=
1
= 0.337 × 106 Ω/km
2πƒCn2π × 50 × 9.49 × 10-3

Reactive volt ampere generated by the line
=
V
=
(132 × 10³)²
= 51703 VAr.
Xc0.336 × 106

= 51703 VAr.