Home » Power Systems » Power systems miscellaneous » Question
  1. What is the overall diameter of a single core cable when its working on a three phase 264 kV system? The maximum permissible stress in the dieletric is not to exceed 20 kV/mm is ________ mm
    1. 21.4 mm
    2. 214 mm
    3. 2.14 mm
    4. .214 mm
Correct Option: A

Effective value (rms) of the phase voltage =
264
= 152.4 kV.
3

Peak value of phase voltage =
264
× √2 = 215.5 kV.
3

For economical size of the cable, optimum ratio of sheath and core radii is given by R/r = e
gmax =
V
=
V
=
V
rIn(R/r)r × 1r

or 20 =
215.5
r

r =
215.5
= 10.7 mm
20

Economical core diameter
= 10.7 × 2 = 21.4 mm