  1. A single line to ground fault occurs on an unloaded generator in phase a. If xd = x2 = 0.25 p.u., x0 = 0.15 p.u., reactance connected in the neutral, xn = 0.05 p.u. and the initial prefault voltage is 1.0 p.u., then the magnitude of the fault current will be ________ p.u.
    1. 375
    2. 3.75
    3. 37.5
    4. 0.375
Correct Option: C