When a line-to-ground fault occurs, the current in the phase is 100 A. The zero sequence current in this case will be _______ A
-
- 1.4996 |202.5°
- 149.96 |200°
- 149.96 |202.5°
- 14900 |202.5°
Correct Option: C
For a L – G fault,
Ia0 = Ia1 = Ia2 and Ia = 3 Ia1
∴ Ia0 = | = | = 33.3 A 212 | ||
3 | 3 |
Ia =(400 + j 100), Ib = (75 – j 600), Ic = (– 300 + j 500)
Ia2 = 1/3 (Ia + α² Ib + αIc)
= | [(400 + j100) + (75 - j 600) |240° + (-300 + j 500)|120°] | |
3 |
= | [400 + j100 + (75 - j 600) + (-300 + j 500)(-0.5 + j0.86)] | |
3 |
= | [(400 + j100) + -553.5 + j235.5 - 280 - j 508] | |
3 |
= | [ - 415.5 - j 172.5] | |
3 |
= 149.96 |202.5°