  1. The sequence components of the fault current are as follows: Ipositive = j1.5 pu, I negative = – j0.5 pu, Izero = – j1 pu. The type of fault in the system is
    1. LG
    2. LL
    3. LLG
    4. LLLG
Correct Option: C

Given, Ia1 = j 1.5 p.u.

Ia2 = – j 0.5 p.u. and, Ia = 1   1   1Ia0
Ib1   α²   αIa1
Ic1   α   α²Ia2

Ia0 = – j 1.0 p.u.
then, Ia = Ia1 + Ia2 + Ia0 = 0.
In case of LLG faults at terminal b, c, the conditions at the faults are characterized by Vb = 0, Vc = 0, Ia = 0, as shown in figure also