  1. Three generators are feeding a load of 100 MW. The details of the generators are given below.
    RatingEfficiencyRegulation
    (MW)(%)(p.u) on 100 MVA base
    Generator-1100200.02
    Generator-2100300.04
    Generator-3100400.03

    In the event of increased load power demand, which of the following will happen?
    1. All the generators will share equal power
    2. Generat or -3 will share more power compared to Generator-1
    3. Generat or -1 will share more power compared to generator-2
    4. Generat or -2 will share more power compared to Generator-3
Correct Option: C

Generators having better regulation will share more power. So generator 1 will share more power than generator 2.