  1. A two machine power system is shown below. Transmission line XY has positive sequence impedance of Z1 Ω and zero sequence impedance of Z0 Ω.

    An ‘a’ phase to ground fault with zero fault impedance occurs at the centre of the transmission line. Bus voltage at X and line current from X to F for the phase ‘a’, are given by Va Volts and Ia Amperes, respectively. Then, the impedance measured by the ground distance relay located at the terminal X of line XY will be given by
    1. Z1
      Ω
      2
    2. Z0
      Ω
      2
    3. (Z0 + Z1)
      Ω
      2
    4. Va
      Ω
      Ia
Correct Option: D

Impedance measured by ground distance relay

=