  1. It is desired to measure parameters of 230 V 115 V, 2 kVA, single-phase transformer. The following wattmeters are available in a laboratory:
    W1 : 250V, 10 A, Low Power Factor
    W2 : 250 V, 5 A Low Power Factor
    W3 : 150 V, 10 A, High Power Factor
    W4 : 150 V, 5 A, High Power Factor
    The wattmeters used in open circuit test and short circuit test of the transformer will respectively be
    1. W1 and W2
    2. W2 and W4
    3. W1 and W4
    4. W2 and W3
Correct Option: D

Open Circuit Test.
On L.V. side, rated voltage applied = 115 V
On L.V. side, current = 2 to 10% of rated current

=
5
×
2000
= 0.869 A
100115

A Since power consumed is less, so low power factor is used.
From available wattmeter,
W2 : 250 V, 5A. LPF used
Short Circuit Test
On H.V. side, rated current applied
=
2000
= 8.69A
230

A and, applied voltage = 5 to 15% of rated Voltage.
=
10
× 230 = 23V
100

Hight power is consumed, so H.P.F used. From available wattmeter, W3: 150 V, 10A. HDF
Hence answer is W2 and W3.