Home » Power Systems » Power systems miscellaneous » Question
  1. A 230 V (phase), 50 Hz, three - phase, 4 – wire system has a phase sequence ABC. A unity power - factor load of 4 kW is connected between phase A and neutral N. It is desired to achieve zero neutral current through the use of a pure inductor and a pure capacitor in the other two phase. The value of inductor and capacitor is
    1. 72.95 mH in phase C and 139.02 μF in phase B
    2. 72.95 mH in phase B and 139.02 μF in phase C
    3. 42.12 mH in phase C and 240.79 μF in phase B
    4. 42.12 mH in phase B and 240.79 μF in phase C
Correct Option: B


Inductor is connected in phase-B and capacitor is connected in phase-C
IB lagging VBN by 90°.
IC leading VCN by 90°.
VAN = 230° ∠0° [VAN is reference phasor)
VBN = 230° ∠– 120
VCN = 230° ∠– 240
Given, IA is drawn at unity pf.

IA =
P
=
4 × 10³
= 17.4∠0°
VANcosφ230

The current into the central will be zero
IB = IC
as IA = IBcos60 + IC cos60
= 2IB sin 60B = √3IB
⇒ IB = IC =
IA
=
17.4
amp = 10.05 A
33

as |IB| = |
VBN
| =
230
ωL(314)L

⇒ L =
230
= 72.86 mH
314 × 10.05

and |LC| = |CCN|. ωC = (230) × 314 × C
⇒ C =
10.05
= 139.08 uf.
230 × 314