A 230 V (phase), 50 Hz, three - phase, 4 – wire system has a phase sequence ABC. A unity power - factor load of 4 kW is connected between phase A and neutral N. It is desired to achieve zero neutral current through the use of a pure inductor and a pure capacitor in the other two phase. The value of inductor and capacitor is
-
- 72.95 mH in phase C and 139.02 μF in phase B
- 72.95 mH in phase B and 139.02 μF in phase C
- 42.12 mH in phase C and 240.79 μF in phase B
- 42.12 mH in phase B and 240.79 μF in phase C
Correct Option: B
Inductor is connected in phase-B and capacitor is connected in phase-C
IB lagging VBN by 90°.
IC leading VCN by 90°.
VAN = 230° ∠0° [VAN is reference phasor)
VBN = 230° ∠– 120
VCN = 230° ∠– 240
Given, IA is drawn at unity pf.
IA = | = | = 17.4∠0° | ||
VANcosφ | 230 |
The current into the central will be zero
IB = IC
as IA = IBcos60 + IC cos60
= 2IB sin 60B = √3IB
⇒ IB = IC = | = | amp = 10.05 A | ||
√3 | √3 |
as |IB| = | | | = | |||
ωL | (314)L |
⇒ L = | = 72.86 mH | |
314 × 10.05 |
and |LC| = |CCN|. ωC = (230) × 314 × C
⇒ C = | = 139.08 uf. | |
230 × 314 |