While measuring power of a three-phase balanced load by the two-wattmeter method, the readings are 100 W and 250 W. The power factor of the load is _________.
-
- 1 to 10
- 20 to 25
- 0.78 to 0.82
- 0.11 to 0.25
Correct Option: C
Power factor,
Cos φ = cos tan-1 | ![]() | ![]() | ||
W1 + W2 |
= cos tan-1 | ![]() | ![]() | ||
250 + 100 |
cos tan–1 [0.742]0
= 0.802 lagging.