  1. In an ideal vapour compression refrigeration cycle, the specific enthalpy of refrigerant (in kJ/kg) at the following states is given as :
    Inlet of condenser : 283
    Exit of condenser : 116
    Exit of evaporator : 232
    The COP of this cycle is
    1. 2.27
    2. 2.75
    3. 3.27
    4. 3.75
Correct Option: A


1– 2 → work done by the compressor
2 – 3 → condenser heat rejected at constant pressure
3 – 4 → throttling
4 – 1 → heat addition in evaporator
Given: h2 = 283 kJ/ kg
h3 = 116 kJ/kg = h4 (from ph curve)
h1 = 232 kJ/kg
We know

C.O.P =
desired effect
=
Cooling effect
work inputwork done by compressor

C.O.P =
h1 – h4
=
232 - 116
= 2.27
h2 – h1283 - 232