In an ideal vapour compression refrigeration cycle, the specific enthalpy of refrigerant (in kJ/kg) at the following states is given as :
Inlet of condenser : 283
Exit of condenser : 116
Exit of evaporator : 232
The COP of this cycle is
-
- 2.27
- 2.75
- 3.27
- 3.75
- 2.27
Correct Option: A
1– 2 → work done by the compressor
2 – 3 → condenser heat rejected at constant pressure
3 – 4 → throttling
4 – 1 → heat addition in evaporator
Given: h2 = 283 kJ/ kg
h3 = 116 kJ/kg = h4 (from ph curve)
h1 = 232 kJ/kg
We know
C.O.P = | = | |||
work input | work done by compressor |
C.O.P = | = | = 2.27 | ||
h2 – h1 | 283 - 232 |